Why does treating the whole NAC load as if it were at the last appliance give a conservative voltage drop result?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3054
- A: Far wire sections really carry less current than assumed
Explanation
In a real circuit, each segment carries only the current of the appliances beyond it. The lumped method assumes full current over the full length, so it overstates the drop and errs on the safe side.