Question 3069 of 344 · NICET Fire Alarm Systems Level II
Which standby duration does NFPA 72 require for the secondary power of an emergency voice/alarm communication system in alarm?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3069
- A: 15 minutes after 24 h standby
Explanation
Voice systems must operate under maximum connected load for 15 minutes after 24 hours of standby. Other fire alarm systems need 5 minutes of alarm after 24 hours.
More questions: Submittal Preparation and System Layout
- 3070Which equipment locations must the shop drawings show besides initiating devices and appliances?
- 3071When should fire alarm shop drawings normally be approved by the AHJ?
- 3072A heat detector listed for 25 ft spacing is installed on an 11 ft smooth ceiling. The multiplier for that height is 0.91. What is the adjusted spacing?
- 3073A heat detector listed for 50 ft spacing is planned for a 30 ft ceiling. The multiplier is 0.34. What spacing applies?
- 3074A 20 ft wide room uses spot smoke detectors with S = 30 ft. Every point must be within 21 ft of a detector. With one row down the center, what is the maximum spacing along the row?
- 3075A speaker set on its 1 W tap produces 84 dBA at 10 ft. What level is expected at 10 ft on the 2 W tap?