A design calls for a sidewall mounted smoke detector. What placement must the drawing show?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3068
- A: Top of the detector 4 in. to 12 in. below the ceiling
Explanation
Sidewall mounted spot smoke detectors must have the top of the detector between 4 in. and 12 in. below the ceiling. Drawings should note the mounting height for installers.
More questions: Submittal Preparation and System Layout
- 3069Which standby duration does NFPA 72 require for the secondary power of an emergency voice/alarm communication system in alarm?
- 3070Which equipment locations must the shop drawings show besides initiating devices and appliances?
- 3071When should fire alarm shop drawings normally be approved by the AHJ?
- 3072A heat detector listed for 25 ft spacing is installed on an 11 ft smooth ceiling. The multiplier for that height is 0.91. What is the adjusted spacing?
- 3073A heat detector listed for 50 ft spacing is planned for a 30 ft ceiling. The multiplier is 0.34. What spacing applies?
- 3074A 20 ft wide room uses spot smoke detectors with S = 30 ft. Every point must be within 21 ft of a detector. With one row down the center, what is the maximum spacing along the row?