A system uses a digital alarm communicator transmitter (DACT). What does NFPA 72 require for its transmission means?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3081
- C: Two separate means, such as two lines or a line plus another path
Explanation
A DACT must be connected to two separate means of transmission, so loss of one does not leave the premises unmonitored. Each path is supervised.