A building has a 30 ft wide by 120 ft long room with a smooth 12 ft ceiling. Spot smoke detectors use S = 30 ft. How many are needed in a single row down the center?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3085
- C: 4
Explanation
120 / 30 = 4 detectors along the length, each 15 ft from the end walls. With a 30 ft width, a single row is 15 ft from each side wall, within the half spacing limit.