A design places two smoke detectors 28 ft apart in a room with a smooth 10 ft ceiling. Each is 10 ft from the side walls. Does this meet the 30 ft spacing rule?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3089
- A: Yes, both distances are within the limits
Explanation
Detectors may be closer than the listed spacing, and the wall distance may be less than half the spacing. 28 ft between them and 10 ft to the walls are both within limits.