Question 3088 of 344 · NICET Fire Alarm Systems Level II
A designer must produce battery calculations. Which current values should be used for each device?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3088
- C: The manufacturer's published standby and alarm currents
Explanation
Battery and voltage drop calculations use the listed standby and alarm currents from the manufacturer's data, so the results reflect the actual equipment installed.
More questions: Submittal Preparation and System Layout
- 3089A design places two smoke detectors 28 ft apart in a room with a smooth 10 ft ceiling. Each is 10 ft from the side walls. Does this meet the 30 ft spacing rule?
- 3090Why should notification appliance circuits be designed with some spare capacity?
- 3001Which item must be shown on fire alarm shop drawings submitted for approval?
- 3002Which document gives the reviewer the logic of what each input does to each output?
- 3003What does a riser diagram show on a fire alarm shop drawing set?
- 3004Which calculation must be included with the shop drawings for a system with secondary power from batteries?