Which calculation must be included with the shop drawings for a system with secondary power from batteries?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3004
- D: A battery standby and alarm calculation
Explanation
Submittals include battery calculations showing standby and alarm loads, the required duration, and the aging correction factor. Voltage drop calculations for NACs are also included.
More questions: Submittal Preparation and System Layout
- 3005Which sheet item helps the reviewer confirm each wall mounted strobe will cover its room?
- 3006What must record drawings show at the end of a project?
- 3007Before laying out devices in an existing building, what is the purpose of a site survey?
- 3008Which ceiling condition found during a site survey changes smoke detector spacing?
- 3009A smooth ceiling room is 60 ft by 90 ft. Detectors are laid out on a 30 ft grid. How many spot smoke detectors are needed?
- 3010A corridor is 10 ft wide. Using the 0.7S rule with S = 30 ft (every point within 21 ft of a detector), what is the maximum spacing between detectors along the centerline?