Question 2009 of 297 · NICET Fire Alarm Systems Level III
How often must manual fire alarm boxes be functionally tested?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2009
- A: Annually
Explanation
Manual fire alarm boxes are functionally tested every year by operating them as the manufacturer instructs and confirming the alarm signal at the control unit. They are also visually inspected for damage and access.
More questions: Maintenance
- 2010Which test frequency does NFPA 72 assign to mechanical (vane) and pressure-type waterflow alarm devices?
- 2011Under NFPA 25, how often must sprinkler control valve supervisory switches be tested?
- 2012How often must audible and visible notification appliances be functionally tested?
- 2013During routine annual testing of an unchanged building, must a technician take sound pressure level readings at every audible appliance?
- 2014A load voltage test shows the fire alarm battery voltage under load falls below the battery manufacturer's minimum. What is the correct action?
- 2015How often must the emergency control functions of a fire alarm system, such as elevator recall and fan shutdown, be tested?