Question 2035 of 297 · NICET Fire Alarm Systems Level III
An intermittent ground fault trouble comes and goes on a system with eight circuits. What is an efficient troubleshooting strategy?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2035
- C: Isolate circuits one at a time, then split the faulty one into halves
Explanation
Ground faults are found by isolation: lift circuits one at a time to find the affected one, then divide that circuit at junction points to narrow down the location. Defeating ground detection hides the problem and violates monitoring requirements.
More questions: Maintenance
- 2036A notification appliance circuit is in trouble. With the field wiring disconnected from the panel, you measure the resistance across the two field conductors and read an open circuit instead of the end-of-line resistor value. What does this indicate?
- 2037A short on a signaling line circuit drops out 120 devices on a large floor. Which design feature limits how many devices are lost to one short?
- 2038During the annual inspection of a 24 VDC system, you measure 27.3 V across the battery terminals with the charger connected. What does this reading usually indicate?
- 2039During the annual test of a duct smoke detector, which check is needed besides the functional alarm test?
- 2040During annual testing of an air-sampling smoke detection system, what transport time requirement applies to the farthest sampling port?
- 2041An addressable smoke detector reports a maintenance alert because its drift compensation has reached its limit. What is the correct response?