Question 2034 of 297 · NICET Fire Alarm Systems Level III

An engine-driven generator serves as part of the fire alarm system's secondary power. Which standard governs its testing?

Exactly one answer is correct.

Show solution

Correct answer to question 2034

  • B: NFPA 110

Explanation

When a generator is part of the secondary supply, NFPA 72 points to NFPA 110 for its inspection, testing, and maintenance. NFPA 13 and NFPA 25 cover sprinkler systems, and NFPA 90A covers HVAC systems.

Next to question ›