During the annual inspection of a 24 VDC system, you measure 27.3 V across the battery terminals with the charger connected. What does this reading usually indicate?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2038
- D: A normal float charge voltage for a 24 V lead-acid battery set
Explanation
A 24 V sealed lead-acid battery is two 12 V batteries in series, and its float charge voltage is typically about 27.0 to 27.6 V. The reading is normal; the battery's condition still has to be confirmed with a load or capacity test per the manufacturer.
More questions: Maintenance
- 2039During the annual test of a duct smoke detector, which check is needed besides the functional alarm test?
- 2040During annual testing of an air-sampling smoke detection system, what transport time requirement applies to the farthest sampling port?
- 2041An addressable smoke detector reports a maintenance alert because its drift compensation has reached its limit. What is the correct response?
- 2042Which personnel does NFPA 72 recognize as qualified to perform inspection, testing, and maintenance of fire alarm systems?
- 2043Before the annual visit at a central station monitored building, what should the technician confirm with the central station operator?
- 2044Annual testing reveals that a beam smoke detector alarms at the correct attenuation filter, but its alignment is off and it reports trouble every few days. What is the right action?