Smoke detectors in a building were installed in January 2024. Following the standard sequence, by when must the second sensitivity test be done?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2057
- C: By January 2027, one alternate year after the first test due by January 2025
Explanation
The first sensitivity test is due within 1 year after installation, so by January 2025. After that, testing is every alternate year, which puts the second test by January 2027. Only after that second test may the interval be extended toward 5 years.