Question 2071 of 297 · NICET Fire Alarm Systems Level III
Which signal type indicates an off-normal condition of a fire suppression system, such as a closed control valve or low air pressure?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2071
- C: Supervisory
Explanation
Supervisory signals report the condition of protection systems and their components, such as valve positions, low air, low temperature, or fire pump conditions. Trouble signals report faults in the fire alarm system itself, such as open or grounded circuits.
More questions: Maintenance
- 2072A sprinkler contractor will close a control valve to repair a branch line. From the fire alarm perspective, how should this be managed?
- 2073What are the duties of a person assigned to a fire watch during a fire alarm impairment?
- 2074A 1990s control unit has no replacement parts available and the manufacturer no longer supports it. What is the best ITM manager recommendation to the owner?
- 2075Your company services 60 buildings. Which practice best supports a compliant ITM program?
- 2076After a building was struck by lightning, the panel shows trouble on several circuits and the communicator. What should the service response include?
- 2077The owner asks whether a smoke detector that tested within its listed range can be left in service despite being 14 years old. What does NFPA 72 base the decision on?