Question 2069 of 297 · NICET Fire Alarm Systems Level III

The panel shows a trouble signal that the building engineer silenced yesterday. The fault has not been repaired. What should the control unit do?

Exactly one answer is correct.

Show solution

Correct answer to question 2069

  • D: Resound the trouble signal at intervals until the fault is fixed

Explanation

A silenced trouble signal must automatically resound at intervals until the fault is cleared, so a fault is not forgotten. NFPA 72 sets the maximum interval at 24 hours unless the system has other approved means.