Notification appliances have been silenced after an alarm on the first floor. A detector on the fourth floor then goes into alarm. What must happen?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2070
- A: The notification appliances must automatically reactivate
Explanation
Silencing must not prevent subsequent alarms from reactivating the notification appliances. A new alarm indicates a new event that occupants need to know about.
More questions: Maintenance
- 2071Which signal type indicates an off-normal condition of a fire suppression system, such as a closed control valve or low air pressure?
- 2072A sprinkler contractor will close a control valve to repair a branch line. From the fire alarm perspective, how should this be managed?
- 2073What are the duties of a person assigned to a fire watch during a fire alarm impairment?
- 2074A 1990s control unit has no replacement parts available and the manufacturer no longer supports it. What is the best ITM manager recommendation to the owner?
- 2075Your company services 60 buildings. Which practice best supports a compliant ITM program?