A sprinkler contractor will close a control valve to repair a branch line. From the fire alarm perspective, how should this be managed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2072
- B: As a planned impairment with notifications, then restore and verify the switch
Explanation
Closing a valve impairs the sprinkler system and produces a supervisory signal. It should be handled as a planned impairment with notifications and interim measures, and the valve and switch must be returned to normal and verified when the work is done.