After a building was struck by lightning, the panel shows trouble on several circuits and the communicator. What should the service response include?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2076
- D: Treat it as an emergency impairment and test all affected parts after repair
Explanation
Lightning can damage circuits, modules, and communicators in ways that are not obvious. The system should be treated as impaired until damaged parts are replaced and all affected functions, including signal transmission, are tested.