Which action best prevents unintentional alarm transmission when a technician must replace a detector on a monitored system?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2086
- A: Put the account on test, disable only that point, then restore it
Explanation
Targeted, documented disabling of just the point being worked on, together with notifying the supervising station, keeps the rest of the system in service. Powering down the whole system or pulling communicator wiring creates a full impairment.
More questions: Maintenance
- 2087Which of these is the correct sequence when a deficiency found during inspection cannot be fixed on the spot?
- 2088Which measurement is typically used when sound pressure levels are verified after a renovation?
- 2089An ITM contract requires a quarterly visual inspection of a central station signaling path that the code requires only annually. Which frequency applies to the service company?
- 2090A client asks why a semiannual waterflow test produced a signal at the central station 75 seconds after the inspector's test valve was opened. Does this meet the requirement?
- 2001A new system with 400 spot smoke detectors was accepted last month. When must the first sensitivity test of those detectors be performed?
- 2002Your service team has completed the first two required sensitivity tests on a building's smoke detectors and every detector was within its listed range both times. What may the ITM manager do?