An existing system tests correctly, but you notice the building's occupancy changed from offices to a daycare. What should your report recommend?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2085
- C: A review of the system against the new occupancy's requirements
Explanation
A change of occupancy can bring new requirements for detection, notification, and monitoring under the IBC, IFC, and NFPA 101. The service company should flag it so the owner and design professional can evaluate compliance with the AHJ.