Question 2087 of 297 · NICET Fire Alarm Systems Level III
Which of these is the correct sequence when a deficiency found during inspection cannot be fixed on the spot?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2087
- D: Document it, notify the owner in writing, add interim measures if needed, repair
Explanation
Deficiencies must be reported to the owner in writing with enough detail to act on. If the deficiency impairs the system, interim measures and the required notifications apply until repairs and retesting are complete.
More questions: Maintenance
- 2088Which measurement is typically used when sound pressure levels are verified after a renovation?
- 2089An ITM contract requires a quarterly visual inspection of a central station signaling path that the code requires only annually. Which frequency applies to the service company?
- 2090A client asks why a semiannual waterflow test produced a signal at the central station 75 seconds after the inspector's test valve was opened. Does this meet the requirement?
- 2001A new system with 400 spot smoke detectors was accepted last month. When must the first sensitivity test of those detectors be performed?
- 2002Your service team has completed the first two required sensitivity tests on a building's smoke detectors and every detector was within its listed range both times. What may the ITM manager do?
- 2003Which method does NOT measure smoke detector sensitivity and therefore cannot be used to satisfy the sensitivity test requirement?