A NAC calculation shows a 5.2 V drop, but only 3.5 V is allowed. Which change will reduce the drop the most?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3008
- C: Splitting the load or using larger wire
Explanation
Voltage drop equals current times resistance. Splitting the circuit cuts the current on each run, and a larger conductor cuts resistance. Raising candela settings increases current and makes the drop worse.
More questions: Submittal Preparation and System Layout
- 3009What is the listed spacing of spot-type heat detectors in a room with a smooth ceiling 9 ft high, if the detector is listed for 50 ft?
- 3010A heat detector listed for 50 ft spacing is installed on a smooth ceiling 15 ft high. The ceiling height multiplier for over 14 up to 16 ft is 0.77. What is the adjusted spacing?
- 3011A heat detector listed for 30 ft spacing is installed on a smooth ceiling 21 ft high. The multiplier for over 20 up to 22 ft is 0.58. What is the adjusted spacing?
- 3012Under the 0.7 rule, how far may a spot-type detector with a nominal 30 ft spacing be from any point on the ceiling?
- 3013On a smooth ceiling, spot smoke detectors at a 30 ft spacing are installed. What is the maximum distance from a detector to a side wall?
- 3014A room is 60 ft by 90 ft with a smooth flat ceiling. Using spot smoke detectors at a 30 ft square spacing, how many detectors are needed?