Question 3010 of 297 · NICET Fire Alarm Systems Level III

A heat detector listed for 50 ft spacing is installed on a smooth ceiling 15 ft high. The ceiling height multiplier for over 14 up to 16 ft is 0.77. What is the adjusted spacing?

Exactly one answer is correct.

Show solution

Correct answer to question 3010

  • A: 38.5 ft

Explanation

Adjusted spacing = listed spacing x multiplier. 50 x 0.77 = 38.5 ft. Ceiling height reductions apply to heat detectors because heat dissipates as the plume rises.