A room is 60 ft by 90 ft with a smooth flat ceiling. Using spot smoke detectors at a 30 ft square spacing, how many detectors are needed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3014
- D: 6
Explanation
Along 60 ft: 60 / 30 = 2 rows, with detectors 15 ft from each wall. Along 90 ft: 90 / 30 = 3 columns. That gives 2 x 3 = 6 detectors.