Question 3012 of 297 · NICET Fire Alarm Systems Level III
Under the 0.7 rule, how far may a spot-type detector with a nominal 30 ft spacing be from any point on the ceiling?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3012
- D: 21 ft
Explanation
The 0.7 rule says all points on the ceiling must be within 0.7 times the selected spacing of a detector. For 30 ft spacing, 0.7 x 30 = 21 ft. This allows irregular rooms to be covered without strict square grids.