Question 3016 of 297 · NICET Fire Alarm Systems Level III
A ceiling has beams 12 in deep spaced 6 ft on center. How is spot heat detector spacing adjusted?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3016
- C: At right angles to the beams, two-thirds of listed spacing
Explanation
For heat detectors, beams over 4 in deep require spacing at right angles to the beams to be no more than two-thirds of the listed spacing. Where beams are over 18 in deep and more than 8 ft apart, each bay is treated as a separate area.