Question 3047 of 297 · NICET Fire Alarm Systems Level III
Where more than two visible appliances are in the field of view, what must the design provide?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3047
- B: Synchronized flashes
Explanation
Visible appliances in the same field of view must be synchronized when more than two are visible, to reduce the risk of photosensitive seizures. Synchronization is typically done by the panel or a sync module.
More questions: Submittal Preparation and System Layout
- 3048A strobe is mounted on the ceiling of a 30 ft by 30 ft room with a 10 ft ceiling. Which table should be used to select its rating?
- 3049In sleeping rooms, what is the minimum visible appliance rating when the appliance is more than 24 in below the ceiling?
- 3050What is the maximum distance allowed between the pillow and the visible appliance in a sleeping room?
- 3051Which document must the designer prepare before a mass notification system is designed?
- 3052A shop drawing shows the pathway class for each circuit. Why is this information important for review?
- 3053A designer must document where pathway survivability Level 2 or 3 is required. Which system type most often triggers this?