A strobe is mounted on the ceiling of a 30 ft by 30 ft room with a 10 ft ceiling. Which table should be used to select its rating?

Exactly one answer is correct.

Show solution

Correct answer to question 3048

  • A: The ceiling-mounted table

Explanation

NFPA 72 has separate room spacing tables for wall-mounted and ceiling-mounted visible appliances, and the ceiling table varies with ceiling height. Using the wall table for a ceiling appliance can result in too low a rating.