Question 3049 of 297 · NICET Fire Alarm Systems Level III
In sleeping rooms, what is the minimum visible appliance rating when the appliance is more than 24 in below the ceiling?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3049
- B: 110 cd
Explanation
In sleeping areas, visible appliances within 24 in of the ceiling must be at least 177 cd. Where the appliance is more than 24 in below the ceiling, 110 cd is permitted. The appliance must also be within 16 ft of the pillow.