Under the IBC, which occupancy requires smoke alarms in sleeping units, even where a fire alarm system is installed?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3070
- D: Group R-1 hotels
Explanation
IBC 907.2.11 requires single- and multiple-station smoke alarms in Group R occupancies, including R-1 sleeping units. Building fire alarm systems with smoke detectors in the unit may serve this purpose where the code allows.