In a fully sprinklered building where most manual boxes were omitted under the IBC exception, how many manual boxes are still required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3068
- A: At least one, at a location approved by the fire code official
Explanation
Where manual boxes are omitted due to sprinkler waterflow activating notification, IBC 907.4.2 still requires at least one manual box in an approved location, typically near the control unit, for supervisory or manual use.
More questions: Submittal Preparation and System Layout
- 3069Under the IBC, which occupancy group requires an automatic smoke detection system in corridors in most cases, such as nursing homes?
- 3070Under the IBC, which occupancy requires smoke alarms in sleeping units, even where a fire alarm system is installed?
- 3071In a high-rise building, which notification system does the IBC require?
- 3072Under NFPA 101, which occupancy generally requires a fire alarm system for any new building regardless of size?
- 3073A plan reviewer notes that the building's code is NFPA 101 and the IBC, and the two disagree on a threshold. How should the designer proceed?
- 3074Why should the design documents state the adopted code editions?