Question 3072 of 297 · NICET Fire Alarm Systems Level III
Under NFPA 101, which occupancy generally requires a fire alarm system for any new building regardless of size?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3072
- A: New health care occupancies
Explanation
NFPA 101 requires fire alarm systems in all new health care occupancies, because patients may be incapable of self-preservation. Storage and parking occupancies have thresholds based on size and use.
More questions: Submittal Preparation and System Layout
- 3073A plan reviewer notes that the building's code is NFPA 101 and the IBC, and the two disagree on a threshold. How should the designer proceed?
- 3074Why should the design documents state the adopted code editions?
- 3075A plan review comment asks you to show the location of the fire alarm control unit and annunciator. What usually governs where they go?
- 3001A panel draws 0.45 A in standby and 2.10 A in alarm. The system needs 24 hours of standby followed by 5 minutes of alarm, and you apply the 1.25 aging correction factor of NFPA 72 (2022/2025). What is the minimum battery capacity?
- 3002A system draws 0.30 A in standby and 1.80 A in alarm. With 24 hours standby, 5 minutes alarm, and no margin, what is the required battery capacity?
- 3003An in-building emergency voice/alarm communications system draws 0.80 A standby and 6.0 A in alarm. What alarm duration must the battery calculation use after the 24-hour standby?