Question 3074 of 297 · NICET Fire Alarm Systems Level III
Why should the design documents state the adopted code editions?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3074
- B: Requirements differ between editions
Explanation
Thresholds and technical rules change from edition to edition, for example new rules in NFPA 72 2025 on panel display heights and record cabinets. Stating the editions makes the design basis clear for review and acceptance.
More questions: Submittal Preparation and System Layout
- 3075A plan review comment asks you to show the location of the fire alarm control unit and annunciator. What usually governs where they go?
- 3001A panel draws 0.45 A in standby and 2.10 A in alarm. The system needs 24 hours of standby followed by 5 minutes of alarm, and you apply the 1.25 aging correction factor of NFPA 72 (2022/2025). What is the minimum battery capacity?
- 3002A system draws 0.30 A in standby and 1.80 A in alarm. With 24 hours standby, 5 minutes alarm, and no margin, what is the required battery capacity?
- 3003An in-building emergency voice/alarm communications system draws 0.80 A standby and 6.0 A in alarm. What alarm duration must the battery calculation use after the 24-hour standby?
- 3004In a battery calculation, which current values should be used for each device?
- 3005A 24 VDC notification circuit has 10 strobes drawing a total of 1.5 A. The farthest strobe is 300 ft from the panel on 14 AWG solid wire with 3.07 ohms per 1,000 ft. What is the approximate voltage drop at the end?