Question 3001 of 297 · NICET Fire Alarm Systems Level III

A panel draws 0.45 A in standby and 2.10 A in alarm. The system needs 24 hours of standby followed by 5 minutes of alarm, and you apply the 1.25 aging correction factor of NFPA 72 (2022/2025). What is the minimum battery capacity?

Exactly one answer is correct.

Show solution

Correct answer to question 3001

  • D: About 13.7 Ah

Explanation

Standby: 0.45 A x 24 h = 10.8 Ah. Alarm: 2.10 A x (5/60) h = 0.175 Ah. Total 10.975 Ah, times 1.25 = 13.7 Ah, so a battery of at least about 13.7 Ah is needed (an 18 Ah battery would typically be selected). Using 1.2 gives 13.2 Ah, which reflects the older 20 percent margin.