A failed smoke detector is replaced with an identical model at the same address. What test is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 1086
- C: Test the replaced device and verify the functions it controls
Explanation
NFPA 72 requires reacceptance testing of replaced or repaired devices and their associated functions. The whole circuit or system does not need a new acceptance test for a like for like replacement.