A submittal shows strobe locations but no candela settings. Under the IBC shop drawing requirements, how should the reviewer respond?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2002
- B: Return it, because the candela rating of each visible appliance must be shown
Explanation
The IBC requires notification appliance information including candela ratings for visible appliances on the shop drawings. Without them the reviewer cannot confirm room coverage or the battery and voltage drop calculations.
More questions: Submittals, Shop Drawings and Records
- 2003Under NFPA 72, which item belongs to the minimum documentation required for every new system?
- 2004Which format does NFPA 72 accept for the sequence of operation in the system documentation?
- 2005You are approving shop drawings drawn by a Level II technician. Which check is most important to confirm the drawings meet NFPA 72 documentation rules?
- 2006A reviewer stamps shop drawings with a status that lets the contractor proceed, provided the marked corrections are made, without a resubmittal. Which status is this?
- 2007A contractor submits a different manufacturer's speaker than the one in the specification as an equal. What must happen before it can be installed?
- 2008A control unit draws 1.8 A in standby and 6.5 A in alarm. Using 24 hours of standby, 5 minutes of alarm and the 1.25 aging correction factor of NFPA 72 (2022/2025), what minimum battery capacity results?