Question 2002 of 243 · NICET Fire Alarm Systems Level IV

A submittal shows strobe locations but no candela settings. Under the IBC shop drawing requirements, how should the reviewer respond?

Exactly one answer is correct.

Show solution

Correct answer to question 2002

  • B: Return it, because the candela rating of each visible appliance must be shown

Explanation

The IBC requires notification appliance information including candela ratings for visible appliances on the shop drawings. Without them the reviewer cannot confirm room coverage or the battery and voltage drop calculations.

Next to question ›