Question 2003 of 243 · NICET Fire Alarm Systems Level IV
Under NFPA 72, which item belongs to the minimum documentation required for every new system?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2003
- A: A written narrative describing the system intent and its design
Explanation
NFPA 72 Chapter 7 requires, at a minimum, a written narrative of the system intent and description, plus riser diagrams, floor plans, a sequence of operation, equipment data and calculations. Business documents are outside the code.
More questions: Submittals, Shop Drawings and Records
- 2004Which format does NFPA 72 accept for the sequence of operation in the system documentation?
- 2005You are approving shop drawings drawn by a Level II technician. Which check is most important to confirm the drawings meet NFPA 72 documentation rules?
- 2006A reviewer stamps shop drawings with a status that lets the contractor proceed, provided the marked corrections are made, without a resubmittal. Which status is this?
- 2007A contractor submits a different manufacturer's speaker than the one in the specification as an equal. What must happen before it can be installed?
- 2008A control unit draws 1.8 A in standby and 6.5 A in alarm. Using 24 hours of standby, 5 minutes of alarm and the 1.25 aging correction factor of NFPA 72 (2022/2025), what minimum battery capacity results?
- 2009A voice evacuation panel draws 2.1 A in standby and 14 A in alarm at full connected load. Without any margin, what battery capacity is needed for 24 hours of standby followed by the required alarm duration for an emergency voice system?