Question 2008 of 243 · NICET Fire Alarm Systems Level IV

A control unit draws 1.8 A in standby and 6.5 A in alarm. Using 24 hours of standby, 5 minutes of alarm and the 1.25 aging correction factor of NFPA 72 (2022/2025), what minimum battery capacity results?

Exactly one answer is correct.

Show solution

Correct answer to question 2008

  • D: 54.7 Ah

Explanation

Standby needs 1.8 times 24, or 43.2 Ah. Alarm needs 6.5 times 5 divided by 60, about 0.54 Ah. The total of 43.74 Ah times 1.25 equals about 54.7 Ah. A reviewer would accept the next standard size above that value. A 20 percent margin (52.5 Ah) is the pre-2022 method.

Next to question ›