Question 2006 of 243 · NICET Fire Alarm Systems Level IV
A reviewer stamps shop drawings with a status that lets the contractor proceed, provided the marked corrections are made, without a resubmittal. Which status is this?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2006
- C: Approved as noted
Explanation
Approved as noted means work may proceed with the noted corrections incorporated. Revise and resubmit requires a corrected submittal before work proceeds, and rejected means the submittal does not meet the requirements at all.
More questions: Submittals, Shop Drawings and Records
- 2007A contractor submits a different manufacturer's speaker than the one in the specification as an equal. What must happen before it can be installed?
- 2008A control unit draws 1.8 A in standby and 6.5 A in alarm. Using 24 hours of standby, 5 minutes of alarm and the 1.25 aging correction factor of NFPA 72 (2022/2025), what minimum battery capacity results?
- 2009A voice evacuation panel draws 2.1 A in standby and 14 A in alarm at full connected load. Without any margin, what battery capacity is needed for 24 hours of standby followed by the required alarm duration for an emergency voice system?
- 2010A NAC uses 14 AWG solid copper with 3.07 ohms per 1,000 ft, runs 300 ft to the last appliance and carries 2.0 A, assumed lumped at the end. Starting from 20.4 V at end of battery life, what voltage is at the last appliance?
- 2011A NAC must carry 2.5 A to the end of a 400 ft run, and the voltage may drop no more than 4.4 V. Using solid copper resistances of 3.07 ohms (14 AWG), 1.93 ohms (12 AWG) and 1.21 ohms (10 AWG) per 1,000 ft, what is the smallest conductor that works?
- 2012A shop drawing shows a single wall mounted strobe in a 40 ft by 40 ft conference room. What is the minimum effective intensity for that appliance based on the NFPA 72 room spacing table?