Question 2009 of 243 · NICET Fire Alarm Systems Level IV
A voice evacuation panel draws 2.1 A in standby and 14 A in alarm at full connected load. Without any margin, what battery capacity is needed for 24 hours of standby followed by the required alarm duration for an emergency voice system?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2009
- D: 53.9 Ah
Explanation
A voice/alarm system needs 24 hours of standby and 15 minutes of alarm at maximum connected load. Standby is 2.1 times 24, or 50.4 Ah, and alarm is 14 times 0.25, or 3.5 Ah, giving 53.9 Ah. Using 5 minutes instead of 15 gives the 51.6 Ah distractor.
More questions: Submittals, Shop Drawings and Records
- 2010A NAC uses 14 AWG solid copper with 3.07 ohms per 1,000 ft, runs 300 ft to the last appliance and carries 2.0 A, assumed lumped at the end. Starting from 20.4 V at end of battery life, what voltage is at the last appliance?
- 2011A NAC must carry 2.5 A to the end of a 400 ft run, and the voltage may drop no more than 4.4 V. Using solid copper resistances of 3.07 ohms (14 AWG), 1.93 ohms (12 AWG) and 1.21 ohms (10 AWG) per 1,000 ft, what is the smallest conductor that works?
- 2012A shop drawing shows a single wall mounted strobe in a 40 ft by 40 ft conference room. What is the minimum effective intensity for that appliance based on the NFPA 72 room spacing table?
- 2013Where must the system record documents be stored?
- 2014The documentation cabinet for a high-rise is placed in the engineering office instead of at the fire command center. What must be provided at the control unit?
- 2016How long must the record of completion and the record drawings be retained?