For an emergency communication system, what must happen to the risk analysis?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2024
- C: It is documented, and access to it may be restricted
Explanation
The ECS risk analysis forms the basis of the design and must be documented. Because it may reveal security weaknesses, NFPA 72 allows access to it to be restricted, with security sensitive information protected.