Which design documents must state the pathway survivability level used for each circuit of a voice evacuation system?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2025
- D: The design documents prepared for the system
Explanation
NFPA 72 requires the design documentation to identify pathway survivability levels, so installers and reviewers know which circuits need 2 hour cable, enclosures or sprinkler protection. A data sheet cannot know the building design.
More questions: Submittals, Shop Drawings and Records
- 2026A voice system design treats storage closets as not requiring intelligible voice. Where must this decision be documented?
- 2031Which item should an ITM inspection and test record include?
- 2032A technician finds that 14 smoke detectors failed sensitivity testing. How should this be documented?
- 2033Shop drawings for an addition to an existing system are under review. Which item is needed to confirm the existing power supply can support the new devices?
- 2035Which piece of information should a Level IV reviewer verify is shown on the floor plans of fire alarm shop drawings?
- 2036Shop drawings show a riser diagram but no indication of conductor type and size. Why should the reviewer return them?