Question 2035 of 243 · NICET Fire Alarm Systems Level IV
Which piece of information should a Level IV reviewer verify is shown on the floor plans of fire alarm shop drawings?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2035
- D: Device locations, room use, ceiling heights and ceiling construction
Explanation
Ceiling height and construction affect detector spacing and appliance selection, so the IBC and NFPA 72 call for these details where they matter. Furniture and finishes do not change code requirements.
More questions: Submittals, Shop Drawings and Records
- 2036Shop drawings show a riser diagram but no indication of conductor type and size. Why should the reviewer return them?
- 2037Which statement describes the security of system documentation under NFPA 72?
- 2038A new control unit is installed in a lobby. Under NFPA 72 (2022/2025), what mounting limits apply to its displays, indicators and controls unless the AHJ permits otherwise?
- 2039When reviewing shop drawings, why should the reviewer compare the control unit's listed equipment with the submitted devices?
- 2040A releasing system submittal is under review. Which item is most important to include?
- 2001You are reviewing a fire alarm submittal before it goes to the building official. Which item does the IBC require on fire alarm shop drawings?