Question 2026 of 243 · NICET Fire Alarm Systems Level IV
A voice system design treats storage closets as not requiring intelligible voice. Where must this decision be documented?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2026
- C: In the design documents, which identify which ADSs need intelligibility
Explanation
The designer defines acoustically distinguishable spaces and identifies which require intelligible voice. Some spaces, such as small closets, may only need audibility. The decision is recorded in design documents so testing can follow it.
More questions: Submittals, Shop Drawings and Records
- 2031Which item should an ITM inspection and test record include?
- 2032A technician finds that 14 smoke detectors failed sensitivity testing. How should this be documented?
- 2033Shop drawings for an addition to an existing system are under review. Which item is needed to confirm the existing power supply can support the new devices?
- 2035Which piece of information should a Level IV reviewer verify is shown on the floor plans of fire alarm shop drawings?
- 2036Shop drawings show a riser diagram but no indication of conductor type and size. Why should the reviewer return them?
- 2037Which statement describes the security of system documentation under NFPA 72?