Shop drawings show a riser diagram but no indication of conductor type and size. Why should the reviewer return them?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2036
- B: Conductor type and size are required items and are needed to check voltage drop and survivability
Explanation
The IBC lists conductor type and size on shop drawings. Without it, voltage drop calculations cannot be checked, and survivability requirements such as 2 hour rated cable cannot be confirmed.
More questions: Submittals, Shop Drawings and Records