Question 2038 of 243 · NICET Fire Alarm Systems Level IV
A new control unit is installed in a lobby. Under NFPA 72 (2022/2025), what mounting limits apply to its displays, indicators and controls unless the AHJ permits otherwise?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 2038
- C: Top item no higher than 6 ft and lowest item not within 15 in. of the floor
Explanation
Control unit displays, indicators and controls must be mounted so that the highest item is not more than 6 ft above the finished floor and the lowest is not within 15 in. of it. The 2025 edition reworded the rule to refer to the top and bottom of textual displays.
More questions: Submittals, Shop Drawings and Records
- 2039When reviewing shop drawings, why should the reviewer compare the control unit's listed equipment with the submitted devices?
- 2040A releasing system submittal is under review. Which item is most important to include?
- 2001You are reviewing a fire alarm submittal before it goes to the building official. Which item does the IBC require on fire alarm shop drawings?
- 2002A submittal shows strobe locations but no candela settings. Under the IBC shop drawing requirements, how should the reviewer respond?
- 2003Under NFPA 72, which item belongs to the minimum documentation required for every new system?
- 2004Which format does NFPA 72 accept for the sequence of operation in the system documentation?