What does pathway survivability Level 2 generally require?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 3011
- D: 2 hour fire rated cable or a 2 hour rated enclosure
Explanation
Level 2 survivability uses 2 hour fire rated circuit integrity cable, 2 hour cable systems, a 2 hour rated enclosure or another approved method. Level 1 relies on a sprinklered building and metal raceway; Level 3 combines sprinklers with 2 hour protection.
More questions: Circuits, Power Supplies and Control Units
- 3012A ground fault develops on a monitored fire alarm pathway. What must the system do?
- 3013What is the purpose of an end of line resistor on a conventional initiating device circuit?
- 3014Which article of NFPA 70 (National Electrical Code) covers the wiring of fire alarm systems?
- 3015A trouble signal is silenced at the control unit but the fault is not fixed. What must happen?
- 3016From what source must the primary power for a fire alarm system come?
- 3017A panel draws 0.25 A in standby and 1.2 A in alarm. With 24 hours standby and 5 minutes alarm, what capacity is needed before margin?