Question 6004 of 183 · Ohio Fire Alarm Certification Exam
Which method may not be used to measure smoke detector sensitivity?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6004
- C: Spraying an unmeasured amount of aerosol into the detector
Explanation
NFPA 72 and OFC 907.8.4.1 prohibit sensitivity measurement with a device that delivers an unmeasured concentration of smoke or aerosol. Canned smoke is fine for a functional test, but it does not measure sensitivity.
More questions: Inspection, Testing and Maintenance
- 6005When must single and multiple station smoke alarms be replaced?
- 6006Non restorable fixed temperature spot type heat detectors have been in service for 15 years. What does NFPA 72 require?
- 6007How are restorable spot type heat detectors functionally tested?
- 6008How is a non restorable fixed temperature heat detector tested in the field?
- 6009How often must manual fire alarm boxes be tested?
- 6010How often must audible and visible notification appliances be tested under NFPA 72?