After the second required sensitivity test, a detector has stayed within its listed range. To what maximum may the interval be extended?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6003
- B: 5 years
Explanation
Once the second calibration test shows the detector within its listed and marked range, the interval may be extended to not more than five years. Records of nuisance alarms must then be kept.