Question 3001 of 153 · Oklahoma Fire Alarm Technician Exam

What is the nominal spacing used for spot-type smoke detectors on a smooth, flat ceiling when no other spacing is required by the manufacturer?

Exactly one answer is correct.

Show solution

Correct answer to question 3001

  • D: 30 ft between detectors

Explanation

NFPA 72 uses a nominal 30 ft spacing for spot-type smoke detectors on smooth ceilings. A 50 ft figure is a common listed spacing for heat detectors, which is a frequent mix-up.